republican-creole
site Search:


 
    All Forums Hot Topics Gallery






how-to block ads


 
Search Topic:
Share Topic
Posting?
Post a:
Post a:
Links: ·Forum FAQ ·diy online
page: 1 · 2 · 3
AuthorAll Replies

laserfan

join:2005-01-14
Blanco, TX

reply to SparkChaser

Re: Surge Protection Residential Whole House

Nice article, "Surge 101" but I was interested to get to the punch line, which is always "what's this guy selling" and so I looked it up:

»www.bb-elec.com/product_family.a···Trail=94

$100 bucks and applies to only RS22 and 485 lines afaict. Don't sell a three-stage protector for Ethernet it seems. Still, nice info to have.

Bob
Account deleted

join:2012-07-22
New Jersey

It's also curious, because his voltage levels for RS-232 are wrong.



49528867
Premium
join:2010-04-16
Fort Lauderdale, FL
kudos:3

said by Bob:

It's also curious, because his voltage levels for RS-232 are wrong.

Hows that??

Wayne
--
Madness takes its toll, please have exact change ready…

Bob
Account deleted

join:2012-07-22
New Jersey
Reviews:
·Optimum Online

quote:
These shunting devices are most often installed from each data line to the local earth ground, and should be selected to begin conducting current at a voltage as close as possible above the system's normal communications level. For RS-422 and RS-485 systems, the voltage rating selected is typically 5 - 7 volts, in RS-232 systems 12 - 15 volt devices are appropriate.
The voltage spec for RS-232C is -15V to +15V. So by choosing a MOV in the 12 to 15 V range, you'd be shunting signals within the RS-232C spec.

RS-232C devices are required to withstand connection to any voltage in the -25V to +25V range for an indefinite amount of time. (Yes, you can take an RS-232C output pin at +15V and connect it directly to a -25V power supply and let it run all day without damage!)

So a more appropriate MOV device for RS-232C would be in the 20 to 22 V range, not 12 to 15 V as suggested by the author.


49528867
Premium
join:2010-04-16
Fort Lauderdale, FL
kudos:3

Ok that makes sense.

Thanks
Wayne


laserfan

join:2005-01-14
Blanco, TX

Where I live it is common to have the "service entrance" on an outdoor pole, and from there to extend underground to multiple buildings and in different directions from the pole, resulting in sub-panels in each building that are hundreds of feet apart from one another. The only ground rod is at the pole itself, meaning afaict that a lightning strike at any one of these buildings, that finds the wiring therein, only finds ground after traversing say 200 feet to the ground rod at the pole.

Conversely, if a surge event occurs in the overhead wiring and gets through the main panel all-the-way to the remote buildings, then even if you have surge protectors, the excess voltage you need to shunt to ground has to go all-the-way out to the pole again.

Do I have this right, and if yes, how can surge protectors work effectively given the distances to ground? I suppose the answer is: I could add ground rods at each of my buildings and then trench/wire these together between each other and the main service pole/ground. Is this ultimately the right way to do it? Is 6ga enough for a 250' distance?


iknow
Premium
join:2012-03-25

said by laserfan:

Where I live it is common to have the "service entrance" on an outdoor pole, and from there to extend underground to multiple buildings and in different directions from the pole, resulting in sub-panels in each building that are hundreds of feet apart from one another. The only ground rod is at the pole itself, meaning afaict that a lightning strike at any one of these buildings, that finds the wiring therein, only finds ground after traversing say 200 feet to the ground rod at the pole.

Conversely, if a surge event occurs in the overhead wiring and gets through the main panel all-the-way to the remote buildings, then even if you have surge protectors, the excess voltage you need to shunt to ground has to go all-the-way out to the pole again.

Do I have this right, and if yes, how can surge protectors work effectively given the distances to ground? I suppose the answer is: I could add ground rods at each of my buildings and then trench/wire these together between each other and the main service pole/ground. Is this ultimately the right way to do it? Is 6ga enough for a 250' distance?


you should have about 1.024M ohms impedance at 1 ghz with that 6ga 250F wire, so that's not good.


49528867
Premium
join:2010-04-16
Fort Lauderdale, FL
kudos:3

reply to laserfan

said by laserfan:

Do I have this right, and if yes, how can surge protectors work effectively given the distances to ground? I suppose the answer is: I could add ground rods at each of my buildings and then trench/wire these together between each other and the main service pole/ground. Is this ultimately the right way to do it? Is 6ga enough for a 250' distance?

If it where my buildings I would do just that.

Wayne
--
Madness takes its toll, please have exact change ready…


Jack_in_VA
Premium
join:2007-11-26
Mathews, VA
kudos:1

reply to laserfan

said by laserfan:

Where I live it is common to have the "service entrance" on an outdoor pole, and from there to extend underground to multiple buildings and in different directions from the pole, resulting in sub-panels in each building that are hundreds of feet apart from one another. The only ground rod is at the pole itself, meaning afaict that a lightning strike at any one of these buildings, that finds the wiring therein, only finds ground after traversing say 200 feet to the ground rod at the pole.

Conversely, if a surge event occurs in the overhead wiring and gets through the main panel all-the-way to the remote buildings, then even if you have surge protectors, the excess voltage you need to shunt to ground has to go all-the-way out to the pole again.

Do I have this right, and if yes, how can surge protectors work effectively given the distances to ground? I suppose the answer is: I could add ground rods at each of my buildings and then trench/wire these together between each other and the main service pole/ground. Is this ultimately the right way to do it? Is 6ga enough for a 250' distance?


I have a detached garage with a 100 amp panel fed by a 100 amp breaker off the meter base. The contractor/electrician installed a ground rod for the panel. The inspector made him remove the ground wire and run a #6 back to the the main ground rod for the service. He stated only one ground point is permitted.

He did however make us install a second ground rod 5 foot from the existing rod and tie them together with #6 bare copper.

Be careful with advice and the best thing is to consult with your local electrical inspector. You can't go wrong doing that regardless of what you may see here.

nonymous
Premium
join:2003-09-08
Glendale, AZ
Reviews:
·Callcentric

said by Jack_in_VA:

said by laserfan:

Where I live it is common to have the "service entrance" on an outdoor pole, and from there to extend underground to multiple buildings and in different directions from the pole, resulting in sub-panels in each building that are hundreds of feet apart from one another. The only ground rod is at the pole itself, meaning afaict that a lightning strike at any one of these buildings, that finds the wiring therein, only finds ground after traversing say 200 feet to the ground rod at the pole.

Conversely, if a surge event occurs in the overhead wiring and gets through the main panel all-the-way to the remote buildings, then even if you have surge protectors, the excess voltage you need to shunt to ground has to go all-the-way out to the pole again.

Do I have this right, and if yes, how can surge protectors work effectively given the distances to ground? I suppose the answer is: I could add ground rods at each of my buildings and then trench/wire these together between each other and the main service pole/ground. Is this ultimately the right way to do it? Is 6ga enough for a 250' distance?


I have a detached garage with a 100 amp panel fed by a 100 amp breaker off the meter base. The contractor/electrician installed a ground rod for the panel. The inspector made him remove the ground wire and run a #6 back to the the main ground rod for the service. He stated only one ground point is permitted.

He did however make us install a second ground rod 5 foot from the existing rod and tie them together with #6 bare copper.

Be careful with advice and the best thing is to consult with your local electrical inspector. You can't go wrong doing that regardless of what you may see here.

I understand tieing them together with #6 or whatever code requires. The removal of the ground rod after they are tied together?

iknow
Premium
join:2012-03-25

1 edit

reply to 49528867

said by 49528867:

said by laserfan:

Do I have this right, and if yes, how can surge protectors work effectively given the distances to ground? I suppose the answer is: I could add ground rods at each of my buildings and then trench/wire these together between each other and the main service pole/ground. Is this ultimately the right way to do it? Is 6ga enough for a 250' distance?

If it where my buildings I would do just that.

Wayne

it's about 1.024M ohms impedance at 1 ghz with that 6ga 250F wire, so that's good for 60hz, but not lightning, in combination with rods at each building with short heavy connections would take care of that. so this looks good. research lightning protection, sometimes a proper job according to an inspector can conflict with what should be done for lightning protection. the bottom line is, you can't protect from a lightning strike with small, long wires at one point, even if it's nec compliant. research this. there's a license for lightning protection installers, and they do a proper job.

robbin
Premium,MVM
join:2000-09-21
Leander, TX
kudos:1

said by iknow:

research lightning protection, sometimes a proper job according to an inspector can conflict with what should be done for lightning protection.

That shouldn't be a problem if the installation is done according to proper code.

iknow
Premium
join:2012-03-25

said by robbin:

said by iknow:

research lightning protection, sometimes a proper job according to an inspector can conflict with what should be done for lightning protection.

That shouldn't be a problem if the installation is done according to proper code.

you would need a huge cable to have one ground 250 feet long, and have low impedance at 1ghz, which lightning contains. so if electrical code calls for one ground only, that would be very expensive. 1/0 welding cable gets fried by lightning because the individual conductors are too small!.

robbin
Premium,MVM
join:2000-09-21
Leander, TX
kudos:1

Code for Lightning Protection Systems is NFPA 780. Are you saying that it conflicts with NFPA 70 (NEC)?



49528867
Premium
join:2010-04-16
Fort Lauderdale, FL
kudos:3

reply to Jack_in_VA

said by Jack_in_VA:

He did however make us install a second ground rod 5 foot from the existing rod and tie them together with #6 bare copper.

Be careful with advice and the best thing is to consult with your local electrical inspector. You can't go wrong doing that regardless of what you may see here.

That depends on the inspector, for example when the AHJ required you to install an additional ground rod at five feet from the existing ground rod he had you violate NEC 250.53(B).

Rule of thumb when installing additional ground rods they should be spaced at least the length of one (10 feet).

Wayne

--
Madness takes its toll, please have exact change ready…


49528867
Premium
join:2010-04-16
Fort Lauderdale, FL
kudos:3

reply to Jack_in_VA

said by Jack_in_VA:

The contractor/electrician installed a ground rod for the panel. The inspector made him remove the ground wire and run a #6 back to the the main ground rod for the service. He stated only one ground point is permitted.

What a shame he didn't know better.

From my grounding manual published by RO Associates a leader in designing ground systems whose grounding and bonding for communications facilities course I attended a few years back.

»www.protectiongroup.com/Ro-Associates




Wayne
--
Madness takes its toll, please have exact change ready…


49528867
Premium
join:2010-04-16
Fort Lauderdale, FL
kudos:3

reply to iknow

said by iknow:

it's about 1.024M ohms impedance at 1 ghz with that 6ga 250F wire.

Your calculations are way off for a bare direct buried bonding conductor.

Wayne
--
Madness takes its toll, please have exact change ready…

iknow
Premium
join:2012-03-25

reply to robbin

said by robbin:

Code for Lightning Protection Systems is NFPA 780. Are you saying that it conflicts with NFPA 70 (NEC)?

here's a good example of proper protection. »www.tchams.org/FILES/Grounding.pdf

iknow
Premium
join:2012-03-25

reply to 49528867

said by 49528867:

said by iknow:

it's about 1.024M ohms impedance at 1 ghz with that 6ga 250F wire.

Your calculations are way off for a bare direct buried bonding conductor.

Wayne

that was for free air, assuming a .125" conductor 250 FT long.

nonymous
Premium
join:2003-09-08
Glendale, AZ
Reviews:
·Callcentric

reply to 49528867
That is what i am thinking. The one common grounding point should not preclude additional ground rods at the other building. Just the one common point is still needed. Plus I always learned in most basic setups you need a ground rod at both ends of a cable outside. Then on top of that a common ground in most setups even if it is just say a continuous cable sheath.


Tuesday, 21-May 07:09:52 Terms of Use & Privacy | feedback | contact | Hosting by nac.net - DSL,Hosting & Co-lo
over 13.5 years online © 1999-2013 dslreports.com.
Most commented news this week
Hot Topics